J - This is how I see it wired up (complying with the motor's label) :-
It appears the original jumpers were correct.
This is what happens :-
U1U2 appears to be the run winding and is always switched on with the same phasing when running.
V1V2 is the start winding,
You will notice the start coil (V1V2) coil is reversed (with respect to phasing) when starting the other way. This coil is turned off by the cenrifugal switch once the motor is up to speed (70-80% thereof-ish)
(I have used red for live and blue for neutral to show phasing rather than preferred connection - it doesn't actually matter which is which).
I presume the bigger capacitor is the start capacitor.
The smaller capacitor - I suspect - is simply to drain down auto-induced voltages in the start winding - which it does in series with the larger capacitor once the centrifugal switch has opened - which I would presume is of some benefit to performance as well.
Since the smaller capacitor is hard on to the mains when starting - it might serve as a power factor correction capacitor to reduce demand during starting.
Other than that, I can't see what it does.
It's definitely incorrectly connected in the earlier photo you supplied - across the start switch.
I think your problem is partly due to the label diagram - though diagrammatically correct - does not correspond to the physical layout of the terminals.
Hope all this helps.
Regards - Ken
It appears the original jumpers were correct.
This is what happens :-
U1U2 appears to be the run winding and is always switched on with the same phasing when running.
V1V2 is the start winding,
You will notice the start coil (V1V2) coil is reversed (with respect to phasing) when starting the other way. This coil is turned off by the cenrifugal switch once the motor is up to speed (70-80% thereof-ish)
(I have used red for live and blue for neutral to show phasing rather than preferred connection - it doesn't actually matter which is which).
I presume the bigger capacitor is the start capacitor.
The smaller capacitor - I suspect - is simply to drain down auto-induced voltages in the start winding - which it does in series with the larger capacitor once the centrifugal switch has opened - which I would presume is of some benefit to performance as well.
Since the smaller capacitor is hard on to the mains when starting - it might serve as a power factor correction capacitor to reduce demand during starting.
Other than that, I can't see what it does.
It's definitely incorrectly connected in the earlier photo you supplied - across the start switch.
I think your problem is partly due to the label diagram - though diagrammatically correct - does not correspond to the physical layout of the terminals.
Hope all this helps.
Regards - Ken