50,00pm or maybe a factor of or 5 less... it was screaming! I çant remember, but the web will...
On condensers: for a small tug I used concentric copper tubes, steam and condensate outside, pond water drifting through the inside per outlet close to front of screw.very successful, as the pond had an adequate supply of cold.... (In Sunderland there is always an adequate supply of cold everywhere!).
But if you are pumping out a lot of kW of steam from your boiler, getting 1 or 2 kW from a high speed boat engine, then the rest (lots!) Of the kW need a Huge condenser... Look at steam tables for the heat in steam at 1 bar abs at 100C, versus water at 30C, based on the volume of water you boiler will use, and develop the heat flow required at the condenser.... Then look at the radiator on your car - which can take 10 or 15% of the power your engine can develop.... So if you have a 75 kW engine, the radiator can manage maybe 10 to 15 kW? It may give you a clue as to the size of radiator you could need, if you pro-rata size (areas) for your needs.
Does that help?
K