You cannot mix and match AC and DC amperes.
You need to think in terms of power flow, since amperes vary with AC/DC, voltage, etc.
It is a mistake to use watts for any electrical calcuation unless you are sure that the power factor can be ignored or perhaps assumed at 0.80. In the electrical power world, ignoring the power factor is a huge, dangerous and often expensive blunder.
Here are some examples:
A DC motor is operating at 12 VDC, and draws 15.4 amps DC.
So the power used by the motor only is 12 * 15.4 A = 184.8 watts.
We can ignore power factor with DC since it does not come into play with DC.
If you have ever installed a surge tank on a water system, you can understand power factor. A surge tank absorbs the energy from sudden pressure changes in the water, and as the water pressure increases, the surge tank absorbs power, and when the water pressure decreases, the surge tank returns the energy to the system.
So for electrical systems, the magnetic field of motors is the surge tank, and when the voltage alternates (in AC electrical systems), the magnetic field of the motor alternately absorbs and releases energy in the form of electrical current. The current is transferred from the power company to the magnetic field of every motor on the first half cylce of every waveform, and on the second half cycle, this energy is transferred back to the power company. This reactive power does not do any actual work such as rotating the motor, so the power company cannot bill you for power for this, but it does cost the power company money to have to send this power to you, and then receive it back every cycle, so the power companies usually have an added fee for low power factor.
So back to the example, we have a DC motor drawing 15.4 amperes at 12 volts DC, with is using 184.8 watts.
The DC power supply is fed from the AC line, lets say for example at 120 volts AC.
So the current on the AC side must take into account the power that the motor is using, plus the power that the power supply is using in the form of waste heat.
If there was no wasted energy, then the current on the 120 volt side would be 184.8 / 120 = 1.54 amperes AC.
Since the power supply is wasting energy, then the current into the power supply on the 120 volt side will be higher, lets say perhaps 10-20% higher, so maybe 1.84 amperes AC.
Large VFD's generally have a high power factor, usually above 90%.
For AC, the equation is V = I * R * (cos theta), where cos theta is the power factor.
For DC, the equation is V = I * R, since the power factor is 1 in DC systems.
The only way to compare apples to apples is to calculate power first from one side or the other, and then go back to current on the other side using the appropriate voltage and power factor if that applies.
The reason the Edison DC systems did not survive is that the DC currents at low voltages are huge compared to the same size motor operating at a higher voltage.
The line losses are very high in high current DC systems since the line losses are current squared times the resistance of the wire.
The main reason for the use of AC systems is so that you can generate power using an alternator without requiring a high wear/ high maintenance commutator to create DC current. The reason for using high voltage AC systems is because as the voltage goes up, the current goes down, as does the wire size (V = I * R * cos theta), so power companies step up the voltage, transmit the power at low losses, and then step the voltage back down.
Doubling the voltage cuts the current in half. Since copper is expensive, and high currents create a lot of line losses just by heating up the wire due to its internal resistance, then it makes perfect sense to operate a motor or other large load at as high a voltage as is practical and safe.
Many residensial motors can be operated at either 120 volts or 240 volts, single phase.
The general rule of thumb in industry is to operate motors less than 1/2 half horsepower at either 120 volts, or 240 volts single phase.
For motors 1/2 hp and above, and where 3-phase is available, then the motor is generally specified to operate at 3-phase, since the smoothness, efficiency and longjevity of a 3-phase motor will quickly offset any added initial cost.
At around 200 hp, medium voltage begins to become more efficient than low voltage. In the power business, low voltage is defined as voltage 600 volts and lower, and medium voltage is above 600 volts but below 69 KV (69,000 volts). Medium voltage circuits are routinely referred to as "high voltage", but from a design standpoint, that refers to a different system.
Most 500 hp motors are operated at 4.16 KV (4,160 volts), although some operate at higher voltages.
The local refinery has a 32,000 hp air compressor motor that operates I think at 13.2 KV, and is fed from a nearby 161,000 volt line via stepdown transformers.
Every appliance in the US is required to have a nameplate on it, and that nameplate will allow you to calcuate the power, and current that the device uses.
You are generally interested in the input voltage and amperes, not the output voltage and amperes, since if you do not size your input circuit breaker and wire large enough, the wire will overheat, and the breaker will nusiance trip.
A general rule of thumb for power factor in AC circuits is 0.80, unless the nameplate states otherwise.
So the answer to the question is "Generally expect much less AC amperes than DC amperes, since the AC voltage is generally much higher than the DC voltage".
The current valves given on the load side are generally meaningless unless you are actually sizing the wire on the secondary side.
Think in terms of power, and assume most of the power is used by the motor, and some is wasted in the power supply and wiring, so more power always has to be input to a device than you will get out of it via the motor.
Hope this helps more than it muddys the water.
Pat J